I would never take a car to a mechanic to solve an issue, solve it your self and tell 'em what needs replacing.
Brilliant. We Gas Service Engineers love it when punters do that. Surpassed only by those who tell us how long it should take.
I would never take a car to a mechanic to solve an issue, solve it your self and tell 'em what needs replacing.
Brilliant. We Gas Service Engineers love it when punters do that. Surpassed only by those who tell us how long it should take.
Sorry, no simpathy with anyone who chucks parts at a problem, until the problem goes away.
From where did you get the impression that I did?
I didn't, you did that all by yourself..
4 options- either the supply pipe is undersized and always has been, there's an extra appliance been fitted to the line, an obstruction has developed in the line or there's a leak.
Did plumber do a static test? (isolate all appliances, test pressure at meter, isolate supply, test 5 minutes later)- that would tell you if there's a leak in the pipe.
And as someone else, can you report on the size of the supply pipe, the leg lengths and what bends there are (and whether the bends are elbows or wide radius)?
My guess is the pressure drop wasn't measured correctly the previous time (ie under flow conditions) and it hasn't changed. In that case, and since the boiler works normally, the OP doesn't have a problem.1mb is the max drop when installing. If you come across it on a job, excessive pressure drop is only NCS unless it is interfering with another appliance.
I think one can assume that you are not a gas service engineer?
Correct, and never professed to be. As @Harry Bloomfield , every days a school day, what did I get wrong?I think one can assume that you are not a gas service engineer?
Correct, and never professed to be. As @Harry Bloomfield , every days a school day, what did I get wrong?
My guess is the pressure drop wasn't measured correctly the previous time (ie under flow conditions) and it hasn't changed. In that case, and since the boiler works normally, the OP doesn't have a problem.
Pretty much everything, to be honest.
If the installer did it wrongly one year ago, then he needs to be pulled up.
As I understand it, pressure after the meter should be 21+/-2mb, so 17mb would be non-compliant and the gas supplier should rectify it. But if it did fall to 17mb, with pipe drop 20-13.5 = 6.5mb, so something like 11mb at the boiler, the boiler output would be down (unless it has a low-pressure cutout, I wouldn't know)At the moment tge meter pressure appears to be 20mb - what happens if it falls to, say, 17mb?
Brilliant. We Gas Service Engineers love it when punters do that. Surpassed only by those who tell us how long it should take.
If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.
Select the supplier or trade you require, enter your location to begin your search.
Are you a trade or supplier? You can create your listing free at DIYnot Local