Just re read the OP, I had failed to spot it was only fitted a year ago.
How do you know it was 20mb at each end? I may be mistaken but, unless the installer fitted a test point BEFORE the isolation valve, 20 mb would be impossible to achieve as the Vailant test point is on the multifunctional control valve, which itself will incur a 1.5mb drop.
Ideal fit a test point on the isolation valve whereas, I believe, Vailant don’t.
Did you SEE the test?
Was this an independent or , eg, BOXT?
iI would love to hear it was BOXT, tbh.
I would be getting the original installer back. Near in mind that if it was BOXT, Worcester either own it, have shares in it, or there is some other arrangement. I am surprised that the engineer did not make a bigger fuss of , possibly, undersized pipe work - unless they are banned from criticising BOXT?
hi there. No he wasn’t BOXT- he’s independent and certified gas safe engineer. The boiler was installed 2 years ago to replace a 12 year old Vaillant. Definitely no isolation valve on a Valliant.
last year I didn’t see the test, only that everything was ok. This year the nanometer (if that’s what it is called) showed very different readings so Valliant was called to see if the boiler was at fault. It wasn’t. From a Vaillant perspective the 13.5 millibar satisfied their minimum requirements but the plumber is concerned about the pressure drop.
It always seems to be bad news with the boiler although it also transpired that the plumber didn’t fit it as per the instructions as it only has 90mm clearance from the mega flow below and it should be 180mm. That wouldn’t affect the pressure drop.
not quite sure what to do but the plumber is back on Monday.