I have a Vaillant ECO Plus, remote hot water cylinder, wired Honeywell S Plan with a Lifestyle LP722.
This time of year I have CH set to OFF and HW set to twice per day.
For the past day or two, the HW signal calling for heat doesn’t light the boiler. E.g., the boiler water was 19 C this morning despite it set at 60. The boiler status was S.30, which I understand is “no call for heat”. And yet the cylinder thermostat and Lifestyle were definitely calling for heat.
As a test, I turned CH ON and set house thermostat to call for heat; the boiler fired-up from the CH call signal. I then turned CH OFF, and the boiler stayed on, i.e. stayed on only from the HW call signal.
So, in summary, the HW call signal won’t wake up and ignite the boiler, but it will maintain the boiler if the CH call signal is used to wake it up. So strange.
any thoughts?
This time of year I have CH set to OFF and HW set to twice per day.
For the past day or two, the HW signal calling for heat doesn’t light the boiler. E.g., the boiler water was 19 C this morning despite it set at 60. The boiler status was S.30, which I understand is “no call for heat”. And yet the cylinder thermostat and Lifestyle were definitely calling for heat.
As a test, I turned CH ON and set house thermostat to call for heat; the boiler fired-up from the CH call signal. I then turned CH OFF, and the boiler stayed on, i.e. stayed on only from the HW call signal.
So, in summary, the HW call signal won’t wake up and ignite the boiler, but it will maintain the boiler if the CH call signal is used to wake it up. So strange.
any thoughts?