This is on a small-ish caravan/camping park.
The supply into the 'board' is the central SWA with the shroud half way down the sheath. This is a 10mm 3 core SWA, which is bodged into a feed in a barn some 100m away. The barn is fed with 4mm T+E on a 30amp 3036 rewireable, which has been bodged with some copper wire to stop it blowing.
The wylex 60amp Sw-fuse is feeding a shop. The shop has a run of 16mm 3 core SWA. Approx 40m. See the bottom pic of the shop CU.
The little two way CU is feeding a couple rows of hookups. You can't see the outgoing SWA's in the pic, but they are not glanded either. They are 4 and 6mm SWA's, running approx 50m, and feeding 6 hookups each.
Surprisingly this box is now a little tidier - there where a few more bodged SWA's in there last week which have since been removed.
Click for a larger photo:
I know the pic is poor (camera phone). There are a couple 40amp MCB's on ring circuits in this board due to heavy loading in the kitchen takeaway.
Click for a larger photo:
The supply into the 'board' is the central SWA with the shroud half way down the sheath. This is a 10mm 3 core SWA, which is bodged into a feed in a barn some 100m away. The barn is fed with 4mm T+E on a 30amp 3036 rewireable, which has been bodged with some copper wire to stop it blowing.
The wylex 60amp Sw-fuse is feeding a shop. The shop has a run of 16mm 3 core SWA. Approx 40m. See the bottom pic of the shop CU.
The little two way CU is feeding a couple rows of hookups. You can't see the outgoing SWA's in the pic, but they are not glanded either. They are 4 and 6mm SWA's, running approx 50m, and feeding 6 hookups each.
Surprisingly this box is now a little tidier - there where a few more bodged SWA's in there last week which have since been removed.
Click for a larger photo:
I know the pic is poor (camera phone). There are a couple 40amp MCB's on ring circuits in this board due to heavy loading in the kitchen takeaway.
Click for a larger photo: