Hi,
Although I've taken a look through past topics and found problems akin to that being experienced here, just wondered if anyone could help re specifics.
The Boiler
ICOS me3080 Ideal condenser Boiler
The Problem
Seems to occur whilst CH is being supplied, water on it's own is fine. Having been quietly supplying CH for 5-6 hrs we then get the repeated (but not everytime) occurence whilst the boiler transitions from working
(solid green) to flashing (reached set temp) of four to five v loud bangs followed a few seconds later by a screeching sound. Each time this happens we have to check as sometimes the boiler returns the LF code and has to be reset.
It is understood that this may be caused due to poor circulation and overheating.
Actions thus far.
Contacted BGas on a fixed price repair. Over three visits they have thus far changed both actuator valves (water & heating) the Thermistors and this morning cleaned the condense trap etc and finally changed the pump. They also used a magnet to check for sludge in the vicinity of the boiler and turned one radiator with a Drayton valve to max to ensure the CH circuit remains open should all other rads trip off.
The condenser pipe has also been checked for blockages and icing and appears to be fine.
But........ as of 2pm today we still have the same problem!!.
All of the rads bar one were replaced in the summer and all apart from one are fitted with Honeywell stats. The heating is switched on via a room stat and the external boiler controller switched to constant. All rads have heat reaching them.
Any suggestions anyone could provide would be appreciated, following sterling work BGas have now left with mutch head scratching and will probably never return.
Help!.
Although I've taken a look through past topics and found problems akin to that being experienced here, just wondered if anyone could help re specifics.
The Boiler
ICOS me3080 Ideal condenser Boiler
The Problem
Seems to occur whilst CH is being supplied, water on it's own is fine. Having been quietly supplying CH for 5-6 hrs we then get the repeated (but not everytime) occurence whilst the boiler transitions from working
(solid green) to flashing (reached set temp) of four to five v loud bangs followed a few seconds later by a screeching sound. Each time this happens we have to check as sometimes the boiler returns the LF code and has to be reset.
It is understood that this may be caused due to poor circulation and overheating.
Actions thus far.
Contacted BGas on a fixed price repair. Over three visits they have thus far changed both actuator valves (water & heating) the Thermistors and this morning cleaned the condense trap etc and finally changed the pump. They also used a magnet to check for sludge in the vicinity of the boiler and turned one radiator with a Drayton valve to max to ensure the CH circuit remains open should all other rads trip off.
The condenser pipe has also been checked for blockages and icing and appears to be fine.
But........ as of 2pm today we still have the same problem!!.
All of the rads bar one were replaced in the summer and all apart from one are fitted with Honeywell stats. The heating is switched on via a room stat and the external boiler controller switched to constant. All rads have heat reaching them.
Any suggestions anyone could provide would be appreciated, following sterling work BGas have now left with mutch head scratching and will probably never return.
Help!.