PCB Problem on Ideal ISAR HE35, 2years old, worked purfict so far. Customer claims wiff of burning previous week then boiler stops alltogether.
PCB (black case), slightly melted. Opened the box for a peep, transforner is chared, prinary circuit.
Replaced PCB with new orange cased one. Pump turns on but nothing els. not even any codes or neon.
Manual does not cover this.
Ideal suggested a few continuity checks, boiler passed ok. Still dead though.
Ideal claim to bo open on Sunday on website, but office not open on sunday.
Is it me??
power getting to pcb ok.
Had fan out, appears like new, coil reads 11ohms assume its ok.
all therostats measure ok
pump is workig ok.
Honywell diverter measures 7.5Kohm and valve is free.
Gas valve measures 4Kohm, assume is ok.
Condensate trap is clear.
Gas and water pressure are ok.
Conections to pcb are clean secure and buzz out ok.
No water leaks.
any suggestions what to check next
can any part be faulty and have blown new pcb
PCB (black case), slightly melted. Opened the box for a peep, transforner is chared, prinary circuit.
Replaced PCB with new orange cased one. Pump turns on but nothing els. not even any codes or neon.
Manual does not cover this.
Ideal suggested a few continuity checks, boiler passed ok. Still dead though.
Ideal claim to bo open on Sunday on website, but office not open on sunday.
Is it me??
power getting to pcb ok.
Had fan out, appears like new, coil reads 11ohms assume its ok.
all therostats measure ok
pump is workig ok.
Honywell diverter measures 7.5Kohm and valve is free.
Gas valve measures 4Kohm, assume is ok.
Condensate trap is clear.
Gas and water pressure are ok.
Conections to pcb are clean secure and buzz out ok.
No water leaks.
any suggestions what to check next
can any part be faulty and have blown new pcb