I want to wire an immersion heater back in.
I have a couple of spare breakers left in the CU- 2x 32A and 1x 40A. I was hoping for a 20A one. Can I use a 32A or do I need to go for a 20A?
Can we rewind to the beginning.
You are basically creating a new circuit.
Firstly, this needs notifying to the local authority. If you are doing it your self, you need to raise a building notice before you start work (costs £££). When you have finished you'll need to fully test and certify the new circuit (do you have the necerssary calibrated test equipment? It easier and cheaper to use a registered electrician to do the work.
Assuming you are able to do this as a DIY project,
looking at the CU.
The STANDARD domestic radial circuit arrangements are
2.5mm twin and earth protected by a 20amp MCB or
4mm T&E protected by a 32A MCB
As you are a DIYer, I encourage you to stay within these guidelines. (If I found a 2.5mm radial on a 32A MCB during an inspection it would be an unsatisfactory conclusion).
Quite honestly, MCBs are so cheap, why risk putting a cable that has (when installed in ideal conditions) a maximum current-carrying capacity of 27amps on a breaker that is too big for the job? Use a 20, or 16amp MCB.
Your new circuit must be RCD-protected. are your spare MCB positions in an RCD-protected part of the CU?