Came across a RIDDOR reportable situation yesterday. Gas fire removed and electric fire installed. 10mm feed to the gas fir cut off and capped with blue fleixble plastic cap. There was a definate smell of gas in the room but an initial tightness test showed no drop. Anyway I left it on for a further 3 mins and there was an instant drop.
I think what was happening is there was a isolating valve on the 15 mm feed to the fire( reduced to 10 mm) which must have been letting by, the pressure was building up in the 10 mm pipe which had been capped with the plastic cap to the point where it was strong enough for it to push out.
My question is this isolating valve looks just like a water isolation valve, it just had a screw to turn to close/open the valve, all the gas cocks I have seen had a tap/handle of some type. The same type of valve is also fitted to a supply leading to another fire in the dining room. Am I correct about these valves just being for water and not gas?
Open pipe I capped obviously and system is now gas tight but if valves are of incorrect type(ie :don't conform to bs en 331:1998) what does that make the installation AR or NCS?
I think what was happening is there was a isolating valve on the 15 mm feed to the fire( reduced to 10 mm) which must have been letting by, the pressure was building up in the 10 mm pipe which had been capped with the plastic cap to the point where it was strong enough for it to push out.
My question is this isolating valve looks just like a water isolation valve, it just had a screw to turn to close/open the valve, all the gas cocks I have seen had a tap/handle of some type. The same type of valve is also fitted to a supply leading to another fire in the dining room. Am I correct about these valves just being for water and not gas?
Open pipe I capped obviously and system is now gas tight but if valves are of incorrect type(ie :don't conform to bs en 331:1998) what does that make the installation AR or NCS?