Hi Everyone
I have a Belling double oven cooker rated 5.1KW installed in a housing. there is a 45 Amp doublepole switch. The cable is 6mm to a 32 amp RCD Consumer unit.
I have purchased a Belling ceramic hob CHU265 rated at 6.5KW. Is it OK to connect this to the same supply as the cooker. The Belling manuals indicate that you can but a local electician has said I need a new 6mm supply from the Consumer Unit.
Thanks to anyone who comments