Installing a wireless thermostat for glowworm betacom30c

Joined
4 Aug 2016
Messages
3
Reaction score
0
Country
United Kingdom
Hi all, my sisters boiler hasn't got a thermostat and needs to be controlled just via the front panel. I recommended to get a wireless stat to try and moderate the house temps. Ive checked the installation manual and it doesn't give state simply were a two would be connected. Am I right to think that fro the diagram below it should just be a case of removing the "safety thermostat for floor standing" bridge wire and wire in here ?? Ive ordered the same thermostat that i have installed and its takes its mains feed from a fused spur
so doesn't need powering from the boiler. Im happy to mount the receiver and run the wires ready for the gas fitter but i dont want her to be stung £100 for just patching two wires

upload_2021-1-29_9-6-30.png
 
Sponsored Links
just be a case of removing the "safety thermostat for floor standing" bridge wire and wire in here ?
No dont touch that, the stat wires into no 2, 24v RT , but themostat must be a voltage free thermostat.

its takes its mains feed from a fused spur
Has to come from the same circuit as the boiler so the boilers fused spur.

Which thermostat are you fitting ?
 