I plan to install an extra socket near my bathroom door running as a spur from my fuse box (which is on the same wall). What distance should it be from my bath?
From Approved Document Part P explaining various ways in which you can comply with Part P of the Building Regulations (with my emphasis):mapj1 said:Harmonisation will probably allow proper RCD protected sockets in the bathroom one day, but not at the moment I'm afraid.
regards M.
Indeed not, but just like with BS 7671, the Approved Document can only make recommendations and give advice - it has no legal status. And just like the actual law does not require compliance with BS 7671 it does not require compliance with any regulations.mapj1 said:So just using an extension to the UK ring 'to meet Geman regs' is not on.
Well, it's gone now - it was only temporary whilst we had no radiator and plaster to dry off.mapj1 said:Only if you cause an accident with it, and someone complains. .