All,
I have a bathroom above an unheated integral garage and I plan to insulate the floor (about 2.5M x 1.5M) The primary issue is all of the house electrics are bunched together in the middle of the joists (the house was built like this in the 1970s). The joists are 170mm thick (I am aware of the methods, so closest to Method 103 in this case) and the bunching of cables (cooker circuit, ring main, 2 x lighting x circuits). While the house will be rewired, I have to deal with the immediate issue.
The question: what would be acceptable to prevent overheating? e.g would some form of box around the cables (akin to Method A) be acceptable and if so, how large?
Other considerations:
I would like to insulate the entire floor. I have considered Kingspan/Celotex but I also have water and heating pipes running on the top of the joists. Plus I also have to branch off the pipes for other supplies meaning a stiff board construction becomes a little complex - thus I am moving towards rockwool or similar.
When the floor is insulated, I will be lowering the ceiling to create a service void to run cables. This means when any cables that do go through the insulation, it is less than 0.5M to maximise current carrying capability.
I plan to run at least a 10mm cable for an electric shower ready for connection at a later date (ideally to take a 50A), most likely in the service void (as running along the top means it touches the insulation and de-rates to 44A) then up through the floor alongside the foul pipe. For belt and braces, I am considering using XLPE steel wire armour as I understand this has a higher permitted operating temperature. Linked, is there any distance a cable needs to be from water pipes?
The bathroom floor is likely to be covered in luxury vinyl (sub floor is 18mm plywood) and the garage ceiling in fire resistance plasterboard.
Thanks all in advance.
I have a bathroom above an unheated integral garage and I plan to insulate the floor (about 2.5M x 1.5M) The primary issue is all of the house electrics are bunched together in the middle of the joists (the house was built like this in the 1970s). The joists are 170mm thick (I am aware of the methods, so closest to Method 103 in this case) and the bunching of cables (cooker circuit, ring main, 2 x lighting x circuits). While the house will be rewired, I have to deal with the immediate issue.
The question: what would be acceptable to prevent overheating? e.g would some form of box around the cables (akin to Method A) be acceptable and if so, how large?
Other considerations:
I would like to insulate the entire floor. I have considered Kingspan/Celotex but I also have water and heating pipes running on the top of the joists. Plus I also have to branch off the pipes for other supplies meaning a stiff board construction becomes a little complex - thus I am moving towards rockwool or similar.
When the floor is insulated, I will be lowering the ceiling to create a service void to run cables. This means when any cables that do go through the insulation, it is less than 0.5M to maximise current carrying capability.
I plan to run at least a 10mm cable for an electric shower ready for connection at a later date (ideally to take a 50A), most likely in the service void (as running along the top means it touches the insulation and de-rates to 44A) then up through the floor alongside the foul pipe. For belt and braces, I am considering using XLPE steel wire armour as I understand this has a higher permitted operating temperature. Linked, is there any distance a cable needs to be from water pipes?
The bathroom floor is likely to be covered in luxury vinyl (sub floor is 18mm plywood) and the garage ceiling in fire resistance plasterboard.
Thanks all in advance.