insulation resistance o.oo meg

Joined
13 Dec 2008
Messages
3
Reaction score
0
Location
Leeds
Country
United Kingdom
hi would appreciate help with this please
just started testing for part p in domestic dwellings came upon this problem.....for the insulation resistance test on a pme tncs system lighting circuit got reading of 0.00 phase/earth .??? checked as far as could to remove everything from circuit. help.!!!!!!!!!!!!
 
Sponsored Links
Main switch closed, neutral still connected to terminal bar and lamps in circuit? If so then you're seeing the N-E PME connection through a lamp.

Make sure all lamps and are disconnected, the circuit breaker is open and the neutral is removed from the terminal bar.
 
Last time I had there was a screw through a cable :evil:
Thought my R1+R2 was a bit on the good side though :LOL:
 
Sponsored Links
thanks guys had an idea it might be through the neutral to earth will try your suggestions many thanks,,dave
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top