I look at Nest as I pass and Orange, so boiler activated, but can't hear boiler running, the Gen 3 wall thermostat is in about the most central place in the house, but room temperatures are controlled by nine programmable TRV heads, but the oil boiler is a fixed output so cycles off/on as required, but it must cost to heat the pipe work, and if all TRV are closed then pump sucking on a closed system which will likely cause cavitation so can't be good.
I asked for a by-pass valve to be fitted, but seems it will not work with pumps on the return, it is a C plan with DHW thermo syphon no tank thermostat or any motorised valve on DHW.
So if house is satisfied then would be good if pump stopped.
It would seem previous owners did not use central heating, they simply lit a fire, as the central heating was in a mess, they had fitted two pumps, one for main house and one for flat under the house, the flat one was worked by flat thermostat, but main house we had to walk outside down a flight of steps and plug in the pump, and there was no main house thermostat that we could find, found the receiver in the flat, but no thermostat.
On trying to use I found using one pump it would push water in reverse direction on the other system, but with much reduced flow rate, so I could not turn off the flat central heating, and use main house only, or turn off main house and use flat only, so I got a heating engineer to fit two motorised valves, I had expected it to then use one pump, but no, two pumps still fitted, so need a relay with pump to turn on boiler.
Found the main problem was the triple and earth cable main house to flat which should have turned on central heating or DHW changed colours red, yellow, blue to brown, black, grey and one core not connected, seems likely some junction box hidden behind plaster board in flat, so swapped supply from house to flat, and used the two good wires to power Nest Gen 3 in house, so only 12 volt to where ever the junction is. Seemed safer that way.
So the two wires now can control CH and DHW and power the Nest wall thermostat. I brought 4 Energenie TRV heads from old house, and added 5 eQ-3 heads for upstairs and kitchen, and they work well, the boiler does trip out every so often, but other than that is works well, and the boiler will stop once water is hot enough, but that leaves the pump running, likely the TRV heads never fully close so likely still some circulation, there are 14 TRV's in total, although 4 are in flat so not used, yes bathroom towel rail has no TRV but that is thermo syphon so does not really help.
So want the hall wall thermostat to detect when house is warm, and turn off heating, so should I leave doors open or closed on entrance level rooms?
I asked for a by-pass valve to be fitted, but seems it will not work with pumps on the return, it is a C plan with DHW thermo syphon no tank thermostat or any motorised valve on DHW.
So if house is satisfied then would be good if pump stopped.
It would seem previous owners did not use central heating, they simply lit a fire, as the central heating was in a mess, they had fitted two pumps, one for main house and one for flat under the house, the flat one was worked by flat thermostat, but main house we had to walk outside down a flight of steps and plug in the pump, and there was no main house thermostat that we could find, found the receiver in the flat, but no thermostat.
On trying to use I found using one pump it would push water in reverse direction on the other system, but with much reduced flow rate, so I could not turn off the flat central heating, and use main house only, or turn off main house and use flat only, so I got a heating engineer to fit two motorised valves, I had expected it to then use one pump, but no, two pumps still fitted, so need a relay with pump to turn on boiler.
Found the main problem was the triple and earth cable main house to flat which should have turned on central heating or DHW changed colours red, yellow, blue to brown, black, grey and one core not connected, seems likely some junction box hidden behind plaster board in flat, so swapped supply from house to flat, and used the two good wires to power Nest Gen 3 in house, so only 12 volt to where ever the junction is. Seemed safer that way.
So the two wires now can control CH and DHW and power the Nest wall thermostat. I brought 4 Energenie TRV heads from old house, and added 5 eQ-3 heads for upstairs and kitchen, and they work well, the boiler does trip out every so often, but other than that is works well, and the boiler will stop once water is hot enough, but that leaves the pump running, likely the TRV heads never fully close so likely still some circulation, there are 14 TRV's in total, although 4 are in flat so not used, yes bathroom towel rail has no TRV but that is thermo syphon so does not really help.
So want the hall wall thermostat to detect when house is warm, and turn off heating, so should I leave doors open or closed on entrance level rooms?