is my boiler out let to close to an air vent

Joined
12 Nov 2011
Messages
3
Reaction score
0
Location
Essex
Country
United Kingdom
Hi i live in a council house and a guy that serviced my boiler said the outlet which is in the garden is to close to an air vent ,the air vent is about 30 cm below the out let and this vent goes into my kitchen behind the boiler ,is this safe i was told by another guy that came out from the council that its not a problem as heat rises ,also i would like to point out that this is right next to my back door any help would be appreciated thanx
 
Sponsored Links
Depends on what type of flue your boiler has is it a Fan flue or a Balanced Flue natural draught??? ;)
 
Sponsored Links
OK the boiler says Britony combi se

but the cover says chaffoteauy & maury


if thats any help .
 
a fan flued appliance flue must be at least 300mm (in any direction) from an opening of a building, so you will need to measure it carefully
 