Hello all, been a while since I used the forums!
My house has a n F&E tank central heating system with a grundfos aplpha 2 pump and fairly new worcester greenstar ri boiler. For as long as we've lived here Ive always had to run the pump on speed III in order to get heat to distribute to the radiators in the house, and even then was fairly puny down stairs. A few weeks ago I drained the system down - cant even remember why now....After filling up again I initially couldnt get the heating or hot water to fire. Cycling the pump low to high speed and manually releasing air locks around the 3 port valve seemed to help and eventually got the hot water going and the heating vaguely warm. However when heating is on the boiler cuts out repeatedly. The flow pipe from the boiler is always v hot and the return pipe is cool.
As the days went by the heating became gradually worse with downstairs rads getting cooler and cooler and the upstairs not as hot as they used to be.
I had a plumber round as I need some pipe work changing anyway that I couldnt be bothered to do myself - and he reckons I have two problems:
1) At some point in the past our separate feed and vent pipe has been converted to combined feed and vent - resulting in more air locks - so he recommended the original design was re-instated
2) Pump might need replacing
Not wanting to wait till after xmas to have a bit of warmth and being a little doubtful over the benefits of reinstating the separate feed and vent pipes - I decided to reinstate the separate feed and vent pipes myself. I then backfilled the system via the draincock , drained again and then backfilled again and added central heating cleaner. The system was always slow to drain and since backfilling and flushing it now drains alot quicker, suggesting there was a lot of sludge, some of which has now shifted.
However after all this the system performance is if anything worse. I can get the upstairs rads to get moderately hot but none of the downstairs rads are coming on really. Ive recently realised that three of the large downstairs rads are on a drop and these are not coming on atall unless every other rad is turned off.
The pump sounds like its working quite hard on speed III, although is a little noisy. When I cycle through the speed settings it is definitely working but I am convinced now the pump just doesnt have the oomph to push water round the central heating circuit.
Before I take the plunge and get a new pump I thought Id see if anyone thought Id missed anything!? Thanks in advance.....
My house has a n F&E tank central heating system with a grundfos aplpha 2 pump and fairly new worcester greenstar ri boiler. For as long as we've lived here Ive always had to run the pump on speed III in order to get heat to distribute to the radiators in the house, and even then was fairly puny down stairs. A few weeks ago I drained the system down - cant even remember why now....After filling up again I initially couldnt get the heating or hot water to fire. Cycling the pump low to high speed and manually releasing air locks around the 3 port valve seemed to help and eventually got the hot water going and the heating vaguely warm. However when heating is on the boiler cuts out repeatedly. The flow pipe from the boiler is always v hot and the return pipe is cool.
As the days went by the heating became gradually worse with downstairs rads getting cooler and cooler and the upstairs not as hot as they used to be.
I had a plumber round as I need some pipe work changing anyway that I couldnt be bothered to do myself - and he reckons I have two problems:
1) At some point in the past our separate feed and vent pipe has been converted to combined feed and vent - resulting in more air locks - so he recommended the original design was re-instated
2) Pump might need replacing
Not wanting to wait till after xmas to have a bit of warmth and being a little doubtful over the benefits of reinstating the separate feed and vent pipes - I decided to reinstate the separate feed and vent pipes myself. I then backfilled the system via the draincock , drained again and then backfilled again and added central heating cleaner. The system was always slow to drain and since backfilling and flushing it now drains alot quicker, suggesting there was a lot of sludge, some of which has now shifted.
However after all this the system performance is if anything worse. I can get the upstairs rads to get moderately hot but none of the downstairs rads are coming on really. Ive recently realised that three of the large downstairs rads are on a drop and these are not coming on atall unless every other rad is turned off.
The pump sounds like its working quite hard on speed III, although is a little noisy. When I cycle through the speed settings it is definitely working but I am convinced now the pump just doesnt have the oomph to push water round the central heating circuit.
Before I take the plunge and get a new pump I thought Id see if anyone thought Id missed anything!? Thanks in advance.....