Jacuzzi/jetted bathtub

Joined
19 Feb 2016
Messages
6
Reaction score
0
Country
United Kingdom
Stumbled across a jacuzzi/jetted bathtub that is currently connected through a 25A RCD unit as pictured. I have measured the power consumption of the pump and it is 500W with 0.75mm flex. They told me that the RCD unit came with the jacuzzi but I'm adamant that 25A would be too high for this to trip in the event of a fault and it should be a 3A FCU? Also we were going to install IP65 spotlights in the bath panel so I was going to install a new piece of twin and Earth to a 1 gang socket first as the bath panel cannot be removed without a screwdriver.
Cheers.
image.jpeg
image.jpeg
 
Sponsored Links
I'm afraid it may be worse than you think.

The 25A relates to the maximum current the RCD can carry; it is not an overload nor short circuit protection.
An RCD only protects against earth leakage and faults to earth.

There almost certainly should be 3A protection somewhere. Are you sure there isn't?
It could be a single circuit from the CU with a 6A MCB which may be alright unless the manufacturer states otherwise (3A).

Also, the cable connection to the RCD is very poor.




How are you going to switch the light?
 
Yes I have checked and the supply actually comes from a junction box on the kitchen ring so it is on a 32A MCB. The knockouts on the RCD unit haven't been used hence why the cores have just been squeezed in. o_O
 
Sponsored Links
I was going to screw it to the wall underneath the bath
 
How will the householder reset it if it trips? And is it suitable for installation in a bathroom?
 
Yes I have checked and the supply actually comes from a junction box on the kitchen ring so it is on a 32A MCB. The knockouts on the RCD unit haven't been used hence why the cores have just been squeezed in. o_O

If this is accessible are you able to put the RCD here instead of it's current place floating in the air being only supported by the cable terminating into it. Then put a maintenance free box somewhere suitable under the bath
 
Yes I did think of putting the RCD unit in the place of the junction box but this would mean it would be under the floorboards which I thought would make it more inaccessible than being able to unscrew the bath panel.
Thanks.
 
Yes I did think of putting the RCD unit in the place of the junction box but this would mean it would be under the floorboards which I thought would make it more inaccessible than being able to unscrew the bath panel.
Thanks.

Are you an electrician? If not, get somebody who knows what they are doing and leave well alone. If you are......
 
Yes I did think of putting the RCD unit in the place of the junction box but this would mean it would be under the floorboards which I thought would make it more inaccessible than being able to unscrew the bath panel.
Thanks.

Are you an electrician? If not, get somebody who knows what they are doing and leave well alone. If you are......

Not as of yet, no. Just thought this would be something I could tackle myself. I am aware that all this work is notifiable which is what I will then do.

A 13A socket also needs to be fitted due to bath panel spotlights being installed which has a plug-in transformer.

I thought this work would be easy because it cannot be removed without a screwdriver, therefore the space has no zone.

Thanks for your help.
 