Owing to a 'slight accident' while in the loft, I smashed a junction box on the lighting circuit feeding the floor below, so I bought a new one of a well-known brand. This was advertised specifically as a 5A 4-terminal lighting junction box.
The damaged box was rated for 5A and had 4 x 1.0mm cables: feed loop in, feed loop out, switch cable, light-fitting cable. Consequently 3 of the four terminals (L,N,E) each had 3 cable cores, the 4th terminal having just 2 cores. Seems quite normal to me.
Curiously though the new box was labelled for two x 1.5mm cores only. I tried it with 3 x 1.00mm and they did fit enough to get the grub screw to engage, but not very far. I was not happy with the result, so I have replaced it with a larger 20A box instead. Bigger terminals, got the 3 cores in easily, much better grip, so happy with the result.
But....even the 20A box was also marked as two x 1.5mm cores only. What is the point of a 4-terminal box, especially one sold specifically for lighting circuits, if the terminals are sized only for two cores? Or am I misunderstanding something here???
The damaged box was rated for 5A and had 4 x 1.0mm cables: feed loop in, feed loop out, switch cable, light-fitting cable. Consequently 3 of the four terminals (L,N,E) each had 3 cable cores, the 4th terminal having just 2 cores. Seems quite normal to me.
Curiously though the new box was labelled for two x 1.5mm cores only. I tried it with 3 x 1.00mm and they did fit enough to get the grub screw to engage, but not very far. I was not happy with the result, so I have replaced it with a larger 20A box instead. Bigger terminals, got the 3 cores in easily, much better grip, so happy with the result.
But....even the 20A box was also marked as two x 1.5mm cores only. What is the point of a 4-terminal box, especially one sold specifically for lighting circuits, if the terminals are sized only for two cores? Or am I misunderstanding something here???