We have a Kidd VHE boiler with EDGB Inter 2011 burner, Satronic control box and Danfoss BFP21L3 oil pump.
This morning the c.h. did not come on and I found the boiler had locked out. On pressing the reset button the motor runs for 14 secs without firing and then locks out again.
After various checks showed nothing obviously wrong I checked the start up sequence with the burner off, motor disconnected and a bleed pipe on the pump bleed nipple, and the following happens:
1. On pressing the reset button the ignition transformer buzzes and a heathly-looking blue-purple spark appears across the electrodes
2. After 6 secs the solenoid valve clicks and oil runs out of the bleed valve
3. After a further 8 secs the control box locks out and everything stops.
It cannot be the photocell as the boiler never fires in the first place. I have also checked the filter (which was clean), and with the stop tap turned back on there is a plentiful flow of clean oil with no bubbles from the filter housing. I have also cleaned the ignition electrode insulators and changed the nozzle for the one left at the previous service all to no avail.
With the pump running and the bleed valve open the flow is not much greater than the flow under gravity which suggests some kind of pump failure - what could have caused the pump to pack up suddenly overnight?
I should perhaps say that we had 500 litres of oil added to a nearly empty tank last week but after this the boiler has been running fine until this morning.
Any suggestions as to what might be wrong or what other tests I can do would be much appreciated
This morning the c.h. did not come on and I found the boiler had locked out. On pressing the reset button the motor runs for 14 secs without firing and then locks out again.
After various checks showed nothing obviously wrong I checked the start up sequence with the burner off, motor disconnected and a bleed pipe on the pump bleed nipple, and the following happens:
1. On pressing the reset button the ignition transformer buzzes and a heathly-looking blue-purple spark appears across the electrodes
2. After 6 secs the solenoid valve clicks and oil runs out of the bleed valve
3. After a further 8 secs the control box locks out and everything stops.
It cannot be the photocell as the boiler never fires in the first place. I have also checked the filter (which was clean), and with the stop tap turned back on there is a plentiful flow of clean oil with no bubbles from the filter housing. I have also cleaned the ignition electrode insulators and changed the nozzle for the one left at the previous service all to no avail.
With the pump running and the bleed valve open the flow is not much greater than the flow under gravity which suggests some kind of pump failure - what could have caused the pump to pack up suddenly overnight?
I should perhaps say that we had 500 litres of oil added to a nearly empty tank last week but after this the boiler has been running fine until this morning.
Any suggestions as to what might be wrong or what other tests I can do would be much appreciated