If supplementary bonding were present (between A and B), the resistance between A & B would be nowhere as great as 0.25Ω - as I implied, it would be pretty negligible.In the top picture, from another forum poster: If the resistance between point A and B is 0.25ohm ...
As above, the resistance of the SB conductor would be very small so, even if 200A flowed through it, the voltage across it would be far less than 50V - e.g. 3 metres of a 4mm² conductor would only have a resistance of about 0.0165Ω (hence a pd of only about 3.3 V if 200A were flowing through it. Furthermore, only part of the fault current would go through the SB conductor, the rest (maybe even most) of it going through the CPC..... then with a fault current of 200 A causing instantaneous trip of the OPCD then the voltage would be 50V ?
So you are now agreeing it wouldn’t be 144V ??Yes, but I was asking Equitum for him to say; not because I didn't know.
Fair enough, but I thought you were questioning the value of supplementary bonding. You now seem to be agreeing that, in practice, it will always limit touch voltages to 'very safe levels'?I agree with all of the above, I used 0.25ohm to show how big the resistance would need to be before a safe level of 50V was exceeded even with a large fault current and ignoring parallel path of the ECP.
As I've explained, even if the main bonding is 'totally sound', in the absence of supplementary bonding there is still a risk of 'dangerously high' touch voltages (until the fault is cleared by a device).Back to my initial post - supplementary bonding where main bonding is sound is like putting nuts on your granola.
Fair enough, but I thought you were questioning the value of supplementary bonding. You now seem to be agreeing that, in practice, it will always limit touch voltages to 'very safe levels'?I agree with all of the above, I used 0.25ohm to show how big the resistance would need to be before a safe level of 50V was exceeded even with a large fault current and ignoring parallel path of the ECP.
I think you are probably missing the point ...No - I’m saying that without supplementary bonding the resistance of the ECP and the CPC from the diagram without Supp. Bonding is likely to be much less than 0.25ohm just through main bonding and common CPC’s
Of course - but I'm getting confused about whether you are talking about the situation with, or without, supplementary bonding.Let me put it another way. The supp. Bond cable is to make the resistance between the things you can touch that are extraneous as low as possible. A copper pipe in the bathroom that is connected to the MET by a 10mm2 wire is likely to be in the 0.05 ohm bracket, is it not ?
But without SB, point A is live and point B is connected to earth.I’m talking without supp. bonding. The 2 points A and B are joined by a low resistance path formed by the ECP, pipework and bonding
You're missing the point that (without) SB), during the duration of the fault, a very high current is flowing through the path from A to MET, whereas almost no current (only the current through the victim) is flowing from B to MET.I’m talking without supp. bonding. The 2 points A and B are joined by a low resistance path formed by the ECP, pipework and bonding
They detect tiny currents flowing to earth - including through a person.How is an RCD going to help in that scenario? (Without supp bonding) It isn’t is it ?
.Because the R in the equation R≤50V/Ia can be 1666Ω because Ia is 0.03A.Which begs the question why is it (sup. Bonding) permitted to be omitted if it’s RCD protected and the other criteria are met ?