No problem - we've all been thereYes penny has dropped . The supp bond closes the loop in the earthing arrangement. I see it now. Thanks for being patient.
Yes, of course it will help (will trip if 30 mA or more goes through the victim's body).How is an RCD going to help in that scenario? (Without supp bonding) It isn’t is it ?
Some of the current arriving in the L conductor will return to earth via the victim's body rather than returning in the neutral conductor. The current in the N going through the RCD will therefore be less than that in the L going through the RCD - and it is that ';difference'; (the 'residual current') that will cause the RCD to trip
... because it does work - as above.Which begs the question why is it (sup. Bonding) permitted to be omitted if it’s RCD protected and the other criteria are met ?