Ok so please draw the fault current flow on the diagram with the bond in place somewhere between the tap and the met
Fault current shown in blue, as I see it. Dashed and dotted blue lines showing split into three routes:
via CPC and MET to installations earth
through pipe to earth
through pipe then via MEB and MET to installation's earth
Since negligible current will go though the pipe from B to the point of bonding (which I have labelled "C") (only the tiny current through the victim), points B and C will always be at essentially the same potential.
As for the potential at A (which determines the 'touch voltage A-B), that will, be dependent on the resistance of the path between A and C (i.e. a bit of the CPC and the supplementary bonding conductor). That will usually be pretty negligible, even with very high fault currents -
BUT, whatever it is, as I see it, it is determined by the length (and conductor CSAs) of that path from A to C,
NOT on how close C (the place of SB) is to B (the tap/'point of contact.
In some (maybe many) situations, the resistance of that path (hence potential at A, hence touch voltage) could be lower when point C
NOT at point B (i.e. the tap) - it would seem that it depends entirely on the 'geography' of the pipes and conductors.
,