Length of Cable in Lighting Circuit?
19 Jun 2009
How do you estimate the length of cable in a circuit, in particular a lighting circuit (i.e. with the switched live)?
err, if this is from a diagram, use the scale and measure your intended route. allow 2.5 metres for vertical drops and add 10% fudge factor.
If its an existing cable. measure the R1+R2 value and use the table in the OSG to get the length.
Simples!
Simples!
Surely using the R1 + R2 value to imply the length might mean that you get a longer length if you've got a dodgy connection. I thought it might be the other way round, even in an existing circuit. i.e. estimate the length, then calculate the R1 + R2 to check it is within the tabulated limits? If so, how would I deal with the switches?
Dodgy connections - I do not understand. That phrase is not in my Theasuarus.
R1+R2 is not a tabulated value. It is Zs that is tabulated. You need to check that to confirm that the CPD will trip in the required time.
Can we take a step back. Can you explain what you want to achieve by making these measurements?
In my experience I have never found a lighting circuit in a normal sized house that exceeds the EFLI measurements as a result of too long a cable run. - Even with 1.0mm². Vd may be an issue, but its also unlikely.
Ok Step Back - I wanted to do a quick check on a circuit to check that the resistance ties up with the length. So I wanted to estimate the length, and then do the R1 and R2 dead test, looking up the resistance per metre run in the tables to see whether the resistance reading I had taken is less than the length of cable I have estimated.
Having asked the question, there is probably no quick way to do it anyway, and if I am testing the furthest light in the circuit, I only have to worry about the phase switch length to add to the overall circuit length anyway.