Sorry, I meant a Ring. Would it be any different if it were a Radial?
The ring final is normally 30 amp fuse or 32 amp MCB/RCBO using 2.5 mm² cable (1.5 mm² is allowed with mineral cable but that is rare). A radial final can have a range of cables sizes, with 2.5 mm² one would expect to see a 20 amp overload, with 4 or 6 mm² a 32 amp over load, but there is nothing to stop a 16 amp overload feeding a radial final with 1.5 mm² cable.
The point is a 2.5 mm² radial can have a branch from it looking at the socket exactly like that of a ring final, but because supplied by a 20 amp fuse, it does not require a fused connection unit to feed more than one socket.
The problem with the radial is volt drop, it is considered (although no hard and fast rule) that a ring final can have 106 meters of cable, when first told I had a problem emulating the calculations.
The design current is taken as 20 amp centre and 12 amp even spread, and the tabulated mV/A/m is corrected, but do same calculations for a radial
and one drops from 106 to 32 meters, so to replace one ring final you need three radials using 2.5 mm². It also means three RCBO's instead of one, so more expensive to use radials to ring finals. Also it is less able to take the inrush, I have seen many a 110 volt yellow brick that worked without a problem on a ring final, but would trip the B20 MCB on a radial final due to inrush.
The problem that I found was the calculations for volt drop are not easy, which is why I wrote a java script program to do it for me, main point the results for a ring final were known, so I could test the program gave me good results.
As to volt drop on a spur, I have never written a program to work it out, and today with RCD protection and switch mode power supplies, not sure the loop impedance is quite as important as in the old days, things like solar panels and EV charging points are often limited to the 207 to 253 volt range to ensure they trip with a loss of PEN, but neither are really DIY jobs so no need to explain further.
However many people ignore the inspecting and testing, and the line - neutral loop impedance is not recorded, only the line - earth, and this is calculated as a B = 3 to 5, C = 5 to 10 and D = 10 to 20 times the thermal cutout setting, plus 5% safety margin, so B32 need to be able to supply 32 x 5 x 105% = 168 amp, so 230/168 = 1.37 Ω, the problem is the cheap plug in testers are designed for 20 amp as used with rest of Europe, so the pass figure is often 1.9 Ω great for when using a B20 which needs 2.19 Ω but not really much good with a ring final.
So instead of a tester costing £50 you need a tester costing around £200, OK should also test the RCD and insulation resistance etc, but it means to inspect and test a ring final you need a low ohm ohmmeter (must use 200 mA so multi meter no good) or a loop impedance tester. So the fused spur you can test with the cheap £50 tester and most radials, so for the DIY man the fused spur seems the best option.
The Martindale EZ365
does a reasonable job, at around £65.34 both loop and RCD, although it does not measure the time, and 40 mS is not really some thing one can measure with a stop watch. But good enough for most radial finals to test them.
We are looking at near enough here, and can't really say they all OK, but unlikely you will have a problem if it shows OK, and if we expect the DIY to buy the full test kit, I think we are living in cloud cuckoo land.