We are currently rewiring our house and will be commensing the lighting circuits in a few weeks.
I will be installing X10 home automation products on the lighting circuits to allow remote switching and control by the fire/burgular alarm system. You can install the X10 modules in the back boxes, but can only fit one in the backbox (unless you put 40+mm boxes in the wall). Tthis will be a problem if you have a 2+gang switch.
The alternative is to install these modules in JBs, but as everyone know, if you use them they have to be 'accessible' for inspection.
What I am thinking of doing is for each of the 3 lighting circuits (I live in a Town House), is to fit a box somewhere on each floor and install all the JBs with the X10 modules in this box.
So you will have the circuit coming in to the box from the CU looping through all the JBs. The JBs with then obviosuly have cables going to the switch(es) and light(s). This will result in some extra cabling etc, but it will mean that I will have complete control and accessibilty in the future if anything needs changing.
Looking at the Onsite guide there is a limit of 100m of cable. What am I actually measuring for the 100m? Is it the main circuit, switch cable length and lighting cable length?
Can any one see any other regulation issues with this setup? BTW, as I have already started the rewire, I am only bound by 16th Ed, as told to me by the LABC subcontractor.
Cheers
Ad.
I will be installing X10 home automation products on the lighting circuits to allow remote switching and control by the fire/burgular alarm system. You can install the X10 modules in the back boxes, but can only fit one in the backbox (unless you put 40+mm boxes in the wall). Tthis will be a problem if you have a 2+gang switch.
The alternative is to install these modules in JBs, but as everyone know, if you use them they have to be 'accessible' for inspection.
What I am thinking of doing is for each of the 3 lighting circuits (I live in a Town House), is to fit a box somewhere on each floor and install all the JBs with the X10 modules in this box.
So you will have the circuit coming in to the box from the CU looping through all the JBs. The JBs with then obviosuly have cables going to the switch(es) and light(s). This will result in some extra cabling etc, but it will mean that I will have complete control and accessibilty in the future if anything needs changing.
Looking at the Onsite guide there is a limit of 100m of cable. What am I actually measuring for the 100m? Is it the main circuit, switch cable length and lighting cable length?
Can any one see any other regulation issues with this setup? BTW, as I have already started the rewire, I am only bound by 16th Ed, as told to me by the LABC subcontractor.
Cheers