Do you require a building warrant for any of the works?
(are you doing works that may require a warrant - such as moving /altering walls, loft conversion, extension)
If the answer is yes then you may require to comply to the disabled thing.
Generally all work (alterations requirng a warrant) should be disabled adapted. Is you have no level access (steps front and back) you may not be required to.
Check with your local building standards (email or letter) and then you will get a reply in writing for your records.
http://www.sbsa.gov.uk/tech_handbooks/th_pdf_2008/domestic/chapters/Section_4_Domestic_2008.pdf
Outlets and controls of electrical fixtures and systems should be positioned at
least 350 mm from any internal corner, projecting wall or similar obstruction
and, unless the need for a higher location can be demonstrated, not more
than 1.2 m above floor level. This would include fixtures such as sockets,
switches, fire alarm call points and timer controls or programmers. Within
this height range:
• light switches should be positioned at a height of between 900 mm and
1.1 m above floor level.
• standard switched or unswitched socket outlets and outlets for other
services such as telephone or television should be positioned at least 400
mm above floor level. Above an obstruction, such as a worktop, fixtures
should be at least 150 mm above the projecting surface.
Where socket outlets are concealed, such as to the rear of white goods in a
kitchen , separate switching should be provided in an accessible position, to
allow appliances to be isolated.
domestic | safety | danger from accidents | 2007
4.8.5 — 4.8.5