I have a trussed roof space in my 20 year old house which has floor and ceiling joists 70mm deep set at 600mm apart. Currently the floor is filled with a fibreglass blanket to the height of the joists (only 70mm).
My "problem" is to increase the insulation to meet building regulations and also to board the majority of the central loft space with suitable boarding so I can better use it as a storage space. I intend to board the useable space, an area which will measure 5000mm by 7200mm (12 joists). This will leave an area around the boarded space which is not usable for storage anyway because it is too close to the eaves.
Progress so far:
1. I can't simply board over the existing insulation as it is insufficient.
2. From the above measurements, the perimeter is 24.4m and the area is 36m2. Therefore the perimeter/area ratio is 0.677.
3. The building regs mean i am looking to achieve a u value design of 0.16. (I never understand why people keep saying 270mm depth because doesn't it depend what material one is using and their area/perimeter ratio?)
4. Using the calculator on the Celotex website I calculate that I will need around 110mm thickness of Celotex GA3000 which comes in boards that are designed to cut to fit 600mm spaced joists. Does this calculation seem right?
OK, that's about where I have got up to so far. Moving on, the plan is:
1. Take out the existing blanket and replace with 50mm thick Celotex (or equivalent).
2. Board over this.
3. Use the removed fibreglass blanket to top up the surrounding 70mm fibreglass blanket to, say, 210mm (leaving ventilation space at the eaves).
Now, coming to the crux of the matter as I am still 60mm thickness of insulation short.
1. Could I fit further 60mm thick Celotex between the roof joists and would this give me the desired result???
i.e. 50mm between the floor joists plus 60mm between the roof joists.
2. I have based my thinking on Celotex but is there any alternative that would better help me acheived my "simple" objective of a boarded loft that is insulated to building regs?
3. I have not considered the insulative properties of the floor boarding itself. How does this change the above calculations? Not sure what my joiner is going to use?
Would appreciate any advice on any of the above from someone who knows what they are talking about (as I clearly don't!)
Many thanks.
My "problem" is to increase the insulation to meet building regulations and also to board the majority of the central loft space with suitable boarding so I can better use it as a storage space. I intend to board the useable space, an area which will measure 5000mm by 7200mm (12 joists). This will leave an area around the boarded space which is not usable for storage anyway because it is too close to the eaves.
Progress so far:
1. I can't simply board over the existing insulation as it is insufficient.
2. From the above measurements, the perimeter is 24.4m and the area is 36m2. Therefore the perimeter/area ratio is 0.677.
3. The building regs mean i am looking to achieve a u value design of 0.16. (I never understand why people keep saying 270mm depth because doesn't it depend what material one is using and their area/perimeter ratio?)
4. Using the calculator on the Celotex website I calculate that I will need around 110mm thickness of Celotex GA3000 which comes in boards that are designed to cut to fit 600mm spaced joists. Does this calculation seem right?
OK, that's about where I have got up to so far. Moving on, the plan is:
1. Take out the existing blanket and replace with 50mm thick Celotex (or equivalent).
2. Board over this.
3. Use the removed fibreglass blanket to top up the surrounding 70mm fibreglass blanket to, say, 210mm (leaving ventilation space at the eaves).
Now, coming to the crux of the matter as I am still 60mm thickness of insulation short.
1. Could I fit further 60mm thick Celotex between the roof joists and would this give me the desired result???
i.e. 50mm between the floor joists plus 60mm between the roof joists.
2. I have based my thinking on Celotex but is there any alternative that would better help me acheived my "simple" objective of a boarded loft that is insulated to building regs?
3. I have not considered the insulative properties of the floor boarding itself. How does this change the above calculations? Not sure what my joiner is going to use?
Would appreciate any advice on any of the above from someone who knows what they are talking about (as I clearly don't!)
Many thanks.