Logic Combi 30 boiler - no water from hot water taps

Joined
20 Dec 2015
Messages
2
Reaction score
0
Country
United Kingdom
I had an F1 fault code (low water pressure) which I sorted out. Water pressure now 1.5. I've had this prob before about a year ago and easily rectified with no further problems. This time, after rectifying this I am unable to get any water from my hot water tap. Cold water normal flow. Is this just a co-incidence or is there something I need to adjust on the boiler. It is not showing any fault codes. It's Sunday today so tomorrow I will contact my water supplier. Can anyone give advice. Much appreciated.
 
Sponsored Links
you probably turned a valve off under the boiler when you re-pressurised your system
 
you probably turned a valve off under the boiler when you re-pressurised your system
I would say you definately did as algas said. Seen it loads of times with the logics. RHS (return)handle needs to be pointing up/down (same orientation as LHS (flow) handle.
 
Sponsored Links
Thanks so much for your quick replies, not at home at the moment so will do that tomorrow and send reply when sorted. Really appreciate your help. Elaine
 