My understanding is a 2.5mm ring main with a 32A mcb and RCD protection can supply 100m2 floor area, and is limited to 66 m cable to comply with the 4% voltage drop rule.
I need to supply a wing of a new house which is too far away to manage only 66m cable. I could increase the cable to 4mm which would reduce resistance, hence increase length allowed. However as the room is quite small I was thinking of reducing the MCB to 20A (which would allow 106m cable with a 4% voltage drop). Is this allowed, and if so what is the maximum floor area I can supply (?is it still 100m2 or less)
I need to supply a wing of a new house which is too far away to manage only 66m cable. I could increase the cable to 4mm which would reduce resistance, hence increase length allowed. However as the room is quite small I was thinking of reducing the MCB to 20A (which would allow 106m cable with a 4% voltage drop). Is this allowed, and if so what is the maximum floor area I can supply (?is it still 100m2 or less)