Lukewarm water Biasi - low flame for DHW

Joined
13 Jan 2016
Messages
65
Reaction score
0
Country
United Kingdom
I have a Baisi m90e24s combi. Since I moved in a month ago, have only had lukewarm water though it runs much warmer when running dhw at lower pressure. The flame burns visibly lower for DHW then for CH - there are no problems with CH or rads.
Engineer checked it the other day and suggested it might need a new heat exchanger and sensor. Gas flow was fine and dhw dial is turned to max.

Is it possible that cleaning the primary heat exchanger would be enough to fix this - rather than spending £200+ on getting a new primary heat exchanger fitted?

Or could it be caused by another issue?
 
Sponsored Links
"Moved in" ? Are you renting the property?

I can say you don't need a new main heat exchanger but you do need a new engineer.

I need the answer to my first question before I advise you further.

Where do you live?

Tony
 
Hi Tony,

I own the property but bought less than a month ago. It's in East London
 
I would be virtually certain that it is not the main heat exchanger.

But there are many possibilities as to the cause and many are gas related which we don't advise on here.

However I would expect that the cost would range from under £100 to about £180 maximum based on my charges.

But obviously I have not seen your boiler and can only base that assessment on my experience of fixing that model of Biasi.

Tony
 
Sponsored Links
Sealed, for hot water, flame would actually be larger than for central heating (if heating has been on for a while and is up to temperature)

Check the amount of water hot tap deliver at full flow over 15 seconds, multiply by 4 and answer should be about 9.5 litres.
 
Sealed, for hot water, flame would actually be larger than for central heating (if heating has been on for a while and is up to temperature)

Check the amount of water hot tap deliver at full flow over 15 seconds, multiply by 4 and answer should be about 9.5 litres.

Have just checked twice and the amount is 5.6 - 6.4 litres.

Water is initially hot then cold and is then lukewarm btw
 
If moving the black box up or down changes the flow then I'm puzzled because the flow has remained the same whether fully up or down at around 6.9l. Flow switch problem too?
 
Last edited:
Sealed, for hot water, flame would actually be larger than for central heating (if heating has been on for a while and is up to temperature)

Check the amount of water hot tap deliver at full flow over 15 seconds, multiply by 4 and answer should be about 9.5 litres.

Have just checked twice and the amount is 5.6 - 6.4 litres.

Water is initially hot then cold and is then lukewarm btw

5.6-6.4 l per minute?
 
Sealed, for hot water, flame would actually be larger than for central heating (if heating has been on for a while and is up to temperature)

Check the amount of water hot tap deliver at full flow over 15 seconds, multiply by 4 and answer should be about 9.5 litres.

Have just checked twice and the amount is 5.6 - 6.4 litres.

Water is initially hot then cold and is then lukewarm btw

5.6-6.4 l per minute?

Yes. I repeated a few more times and it was close to 6.9 l/min.
 
In that case would be looking to see if the gas line is correctly size for blocked
Not a task end user might undertake
 