Main 24HE - CH hot when DHW is called

Joined
23 Jul 2017
Messages
28
Reaction score
4
Country
United Kingdom
Hi all,

After many faithful years, my boiler has started playing up! When DHW is called, both micro switches on the diverter are engaged (pins push out) despite the CH being off. A new diverter has been fitted, along with new PCB and AAV (old one was leaking). Boiler is a Main 24HE combi.

Does anyone have any ideas add to what it could be? Cheers in advance for any thoughts!
 
Sponsored Links
When the new diverter was fitted, were the sensing tubes checked and cleaned? What was the whole diverter replaced, and why was the pcb replaced?
 
Hi @CBW ,

Thanks for the reply. Sensing tubes checked no, diverter replaced upon recommendation, PCB replaced due to continual flashing power light. PCB cured the power light issue, problem with CH coming on remains!
 
Sponsored Links
Thanks Picasso, something for me to check out. Interestingly, I emailed the diverter valve supplier originally assuming it was faulty, and they've told me it's likely a pump fault. It appears to be working fine to me, do you think there's a chance it could cause this?
 
A faulty pump will not bring the heating on. A blocked plate heat exchanger can send water down the flow pipe
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Sponsored Links
Back
Top