Hi all,
Thanks to all those who've helped me out so far this week - really appreciated.
Now onto another question regarding my supply and earthing this time.
First, a bit of history. The house was built in 1959 and has, as far as I can tell, a TN-S supply arrangement.
In addition to the original CU that serves the main house circuits a small, dedicated CU has been added for an immersion heater, probably put in during the 60s. This second CU has a flat strap - not cable - which is connected to the sheath of the icoming supply in order to provide an earth.
Now, the main CU for the other circuits in the house is *NOT* connected to this earthing strap or the cable sheath in any visible way. It is possible that the CU is connected to the incoming water pipe which I know travels underneath the area on its way to the kitchen.
Now for my questions. Is this strap likely to be sufficient as a connection to the cable sheath? With it being flat it's difficult to judge its equivalent cable area which I know should be at least 16mm2. If sufficient, can I connect the original CU and the new CU that I'm installing to this strap? Should I be contacting the DNO to try and get them to come and sort out a decent earthing point?
Thanks in advance for any advice.
Mike
Thanks to all those who've helped me out so far this week - really appreciated.
Now onto another question regarding my supply and earthing this time.
First, a bit of history. The house was built in 1959 and has, as far as I can tell, a TN-S supply arrangement.
In addition to the original CU that serves the main house circuits a small, dedicated CU has been added for an immersion heater, probably put in during the 60s. This second CU has a flat strap - not cable - which is connected to the sheath of the icoming supply in order to provide an earth.
Now, the main CU for the other circuits in the house is *NOT* connected to this earthing strap or the cable sheath in any visible way. It is possible that the CU is connected to the incoming water pipe which I know travels underneath the area on its way to the kitchen.
Now for my questions. Is this strap likely to be sufficient as a connection to the cable sheath? With it being flat it's difficult to judge its equivalent cable area which I know should be at least 16mm2. If sufficient, can I connect the original CU and the new CU that I'm installing to this strap? Should I be contacting the DNO to try and get them to come and sort out a decent earthing point?
Thanks in advance for any advice.
Mike