Maths check
3 Apr 2016
If the shower I want has these requirements can I just check maths with you for combi sizing!
Assuming incoming mains @ 10 degrees
8l/60s x 42 degree rise x 4.2 joule = 23.52 (24kw)
10l/60s x 42 x 4.2 joule = 29.4 (30kw)
In colder temperature i.e incoming @ 2 degrees
8l/60s x 50 degree rise x 4.2 joule = 28kw
10l/60s x 50 x 4.2 joule = 35kw
Also;
If the mains incoming is 18l/min what is the proportion of hot to cold used at 40 degrees shower?
I am trying to figure if 30kw is fine for me....."best performance" I really hope that doesn't mean vaguely acceptable!
Water minimum flow rate
For best performance within the specified running pressure range a minimum flow of 8 litres per minute should be available to both inlets.
Water temperature requirements
Maximum hot water temperature: = 80°CRecommended maximum: = 65°CMinimum hot water temperature: = 52°CMaximum cold water temperature: = 20°CThe
you are way over thinking this if what you mean would a 30KW boiler be fine for one shower then the answer is yes
Also;
:rolleyes::rolleyes::rolleyes::rolleyes::rolleyes::rolleyes:
Have you ever measured the cold water temperature?
It's unlikely to fall much below 15C and will normally be about 20C.
That depends on the temperatures of the hot and cold.
For a 40C Shower
Hot 60C & cold 20C: 50% (9l) hot and 50% (9l) cold
Hot 60C & cold 15C: 55.56% (10l) hot and 44.44% (8l) cold
For a 40C Shower
Well I can assure you up here that Ive never seen a main above 12c when Ive commissioned any boiler.