MCB trip problem

Joined
16 Jul 2008
Messages
54
Reaction score
1
Location
Surrey
Country
United Kingdom
I recently wired a new upstairs light and power circuit. (The entire upstairs is being converted from bungalow to house). An electrician then came and checked my work and connected the circuits up to a new consumer unit. A couple of nights ago, a day after some new plastering was done, the MCB for the upstairs lights and the RCD for that side of the board tripped. (I hope i'm using the right terminology). I was lucky i noticed almost at once because it took out the fridge and freezer late at night just as i was retiring downstairs.

Anyway, the RCD switch reset OK, but the MCB would not. It clicked back down immediately with a bit of a nasty bang. I tried for two days to contact the electrician, but he's not picking up or ringing back. So today i reset the MCB and all seemed fine for a minute or so and the upstairs lights worked OK. Then the MCB tripped again.

Could anyone please give me any idea what the problem might be? Thanks in advance.
 
Sponsored Links
Look in the area that was plastered, Wet and juice don't work well together.

Remove all fittings in the plasterers work zone and check for moisture and plaster. Also check for loose or lost terminations in any fittings that were in the same area.
 
Thanks Chri5 - there was only really one switch and one lamp on the light circuit in the plastered room and i can't see anything suspicious there. In fact i tried the circuit with these two fittings disconnected this morning and got the result i described.

I had hoped the fact that there was a delay of up to a minute before the trip might point to something - or at least rule out something?
 
we've had some cold nights

it might also be condensation (humidty from drying plaster) inside an accessory. I always like to brush out backboxes after any plastering or decorating

Agree about inspecting all the recently touched stuff, a wire might have come out e.g. when it was being pushed into the backbox, or nipped by a screw.

Guess how I know that.
 
Sponsored Links
An MCB delay of a minute indicates it is the thermal element in the MCB that tripped. For instance, you might be drawing up to 10 A on a 6 A circuit.
 
...the MCB would not. It clicked back down immediately with a bit of a nasty bang....
and yesterday it was magnetic. Maybe it is drying out, but it could also be copper burning away.
 
Thanks guys. So in practical, non technical terms, might it just sort itself out in time as the plastering dries or should i be doing something? If so, what? As i said, the accessories are removed - just bare/tape insulated wires. And presumably any damp in the power sockets would not affect the lighting circuit?
 
You need an insulation resistance tester to track this fault down or an electrician who knows what he's doing. Focusing on the plastering causing the fault could be the wrong thing to do as it could be completly unrelated. Saying that, was any plasterboarding done afterwards, have you ran your cables in a manner that they may be damaged by screws or nails. have the cables been pulled tight in places, are they ran next to or crossing over heating pipes?
 
the Ego is redundant

and it is not a good translation
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Sponsored Links
Back
Top