FWL_Engineer said:
Adam, there has been a legal requirment for the last 12 years that all appliances in the UK are sold based on a 230V supply, so stating it has a 240V rating is an irrelevence.
What do you mean by "irrelevance"? It is a fact, easily confirmed by looking at the detailed specs, that most, if not all, shower manufacturers quote the 240V rating as the headline figure, not the 230V one.
Remember that the supply can vary from +6% to -10%, consequently the actual supply can vary from 207Vac to 243.8Vac, this being the case, you should assume the rating of the circuit is assumed at 230V.
Certainly take supply variation into account, but there is no need to assume that the performance of the shower is different to what the manufacturer claims. If his stated specification at 230V is 8.7kW, then that is the figure you should use - there is no possible justification for deciding that the "9.5kW" rating applies at 230V.
The Breaker that should be installed is a 50A, whilst this is bigger than usually installed, using a 40A MCB would be a bad idea as the MCB would operating above rating everytime the shower is used, this would seriously impede the long term operational characteristics of the MCB.
8.7kW at 230V = 37.8A
9.5kW at 240V = 39.6A
~9.78kW at 243.8V ~= 40.1A
I'd be surprised if MCBs from reputable manufacturers would be seriously impeded by a 0.25% overload....
I agree that a 45A or 50A would be a
better choice than a 40A, provided that's OK for the cable rating, but that doesn't make a 40A MCB a
bad choice...
And what are the implications of ignoring the manufacturers installation instructions? I don't know the answer to this, but would, technically, the appliance no longer be CE approved if it was not installed in accordance with the instructions?