More than fine for 600W of combined load (say 2 and a half amps between friends), the voltage drop across the length carrying all the current is the only the first 2.1 metres, then it splits (correct me if I am wrong) the first hundred watts gets off at 2.1m +1.6m The remaining 500watts continue to JB3, where another 100watts leaves and the to go to the second light and the rest (now only 400W ) goes via JB4. From JB4, if the longest switch run controls the furthest light, then add them, and add them to the feeds beteen CU and JB4, BUT, remember that most of the cable to JB4 is not carrying the full load.
If not already you will be seeing why we don't normally do these sums in too much detail...
OK, switch controlling it plus + longest lamp line + feed to JB4 grand total is 14.9m + 5.8m switch ~about 20m.
You have stacks in hand my friend. At 600W the max length for voltage drop would be nearly 100m, and that assumes that the long length caries all the current, here it doesn't. From a disconnection point of view you are well in side the limits too.
Insulation wise, if 1mm cable is dangling in the open it is rated at well over 10A, this derates to about half if it is stuck between insulation and a wall or ceiling. Only the 2.1m length is carrying the full load, and this is only circa 2.5A, once again you should be well inside the safety limits, by nearly a factor of two. -Have a look in the Kevinborn guide in the for reference section to see your installation method, but I'd be most surprised if you had any problems at all.
Regards M.