4 bed detached house with 2 bathrooms.
We have just ripped out the old 1960’s one pipe system with gravity HW and pumped CH. The layout is being upgraded to a sealed un-vented 2 pipe system with a system boiler and 210L Megaflo indirect cylinder. Both the boiler and cylinder are being housed together in the garage and CH and HW will be independently controlled with an ‘S’ plan system using 2 x 2-port motorised valves.
I have calculated the CH requirements, which comes to 12 kw (including 5% pipe loss and 10% boiler margin). I am struggling to understand the allowance to add for HW so that the CH does not suffer when both are calling for heat at the same time. Some sites say 2kw, some say 3kw. Personally I think this should be determined by the size of the cylinder and how quick you want the tank heated – am I right?
What I need to understand is how you work out how much heat is going to each of the HW and CH circuits for a given boiler size when they are both calling for heat at the same time? Is it 50/50 split or based, or as I suspect, something more complicated than this as, e.g. length of pipe work on each circuit.
For example, if just added the 3kw allowance for HW and therefore fitted a 15kw boiler, what’s stopping the Megaflo taking more than its 3kw allowance and therefore reducing the heat going to the CH circuit? Just because I added 3kw for HW does not stop the Megaflo, with a massive 24kw rated coil inside, zapping as much heat from the boiler as it can take?
Obviously to ensure both circuits are fully satisfied with no impact on either circuit I would need in excess of 36kw which is rather high just to keep CH happy and get the quickest HW heat up times. However, I’ve worked out that it will take around 4.5kw to heat the full 210L in 3 hours, or around 6.8kw to heat it in 2 hours which is quite acceptable (assuming rise in water temperature from 4 deg to 60 deg). So if I put in an 18kw boiler, how will my CH suffer when both are calling? What determines how much of the 18kw the Megaflo will take and how much the CH will take in each hour?
Any help would be appreciated, but please only comment if you actually have some expertise in this area.
We have just ripped out the old 1960’s one pipe system with gravity HW and pumped CH. The layout is being upgraded to a sealed un-vented 2 pipe system with a system boiler and 210L Megaflo indirect cylinder. Both the boiler and cylinder are being housed together in the garage and CH and HW will be independently controlled with an ‘S’ plan system using 2 x 2-port motorised valves.
I have calculated the CH requirements, which comes to 12 kw (including 5% pipe loss and 10% boiler margin). I am struggling to understand the allowance to add for HW so that the CH does not suffer when both are calling for heat at the same time. Some sites say 2kw, some say 3kw. Personally I think this should be determined by the size of the cylinder and how quick you want the tank heated – am I right?
What I need to understand is how you work out how much heat is going to each of the HW and CH circuits for a given boiler size when they are both calling for heat at the same time? Is it 50/50 split or based, or as I suspect, something more complicated than this as, e.g. length of pipe work on each circuit.
For example, if just added the 3kw allowance for HW and therefore fitted a 15kw boiler, what’s stopping the Megaflo taking more than its 3kw allowance and therefore reducing the heat going to the CH circuit? Just because I added 3kw for HW does not stop the Megaflo, with a massive 24kw rated coil inside, zapping as much heat from the boiler as it can take?
Obviously to ensure both circuits are fully satisfied with no impact on either circuit I would need in excess of 36kw which is rather high just to keep CH happy and get the quickest HW heat up times. However, I’ve worked out that it will take around 4.5kw to heat the full 210L in 3 hours, or around 6.8kw to heat it in 2 hours which is quite acceptable (assuming rise in water temperature from 4 deg to 60 deg). So if I put in an 18kw boiler, how will my CH suffer when both are calling? What determines how much of the 18kw the Megaflo will take and how much the CH will take in each hour?
Any help would be appreciated, but please only comment if you actually have some expertise in this area.