metal shed supply...earthing?

Joined
11 Sep 2007
Messages
77
Reaction score
0
Location
Nottinghamshire
Country
United Kingdom
Advice need ed please..
shed approx 30m from house
double socket ( for lawn mower and the odd power tool drill etc lightweight stuff ) amd light.
Going to use either 6 or 10 mm 3 core SWA from non rcd side of board to a 2 way rcd board in shed.

With the shed being of metal construction do I require an earth rod? or can I use the earth from the SWA and bond to shed?

Many thanks.
Am aware od part p
 
Sponsored Links
just came across exporting earths and from my understanding - dont connect cpc at shed end and fit a rod as per tt system
 
Surely you would only need to TT the shed if your house has a PME (TNCS)supply. If it is TNS surely you can extend the equipontial zone from your house.
 
Sponsored Links
Surely you would only need to TT the shed if your house has a PME (TNCS)supply. If it is TNS surely you can extend the equipontial zone from your house.

You can extend the equipotential zone wether the supply is TN-C-S or TN-S

The only reason an out building is sometimes TT-ed is to avoid having to run a 10.0mm² earth to it to extend the equipotential zone.
 
RF please clarify the following for my own edification.
1. If he decides on the TT option all main equipotential bonding must be carried out at the shed end and this precludes earthing the armour of the supply but you would still use the cpc inside the armour cable to distribute to accessories?
2.If he decides to extend the equipotential zone from his dwelling he has 2 choices. He could use 10mm^2 swa as the cpc will be of sufficient csa to provide MEB. Or does he have to run a 10mm^2 earth regardless of the supply cable size (ie in addition)?
3. Also he talks about 6 0r 10mm^2 cable......surely vastly oversized for his requirements. Without even bothering to get the tables out I would have thought 3core 2.5mm^2 would be more than adequate with as separate 10mm^2 earth run together in a duct or even overhead.
4. Would you consider the shed to be an extraneous conductive part and need to be earthed?
5. What would you personally consider as the best solution to this proposed installation?
 
1. If he decides on the TT option all main equipotential bonding must be carried out at the shed end

Yes. All extraneous conductive parts must be main bonded.

and this precludes earthing the armour of the supply

You should earth the armour at the supply end to protect the cable to ensure it will automatically disconnect the supply in the event of mechanical damage.

This must not be connected the the earthing system in the shed.

but you would still use the cpc inside the armour cable to distribute to accessories?

No, you should install 2 core SWA. The CPC for the final circuits must be connected to the shed MET, along with the main earth from the earth stake, and any MEBs.


2.If he decides to extend the equipotential zone from his dwelling he has 2 choices. He could use 10mm^2 swa as the cpc will be of sufficient csa to provide MEB.

As long as the SWA is 3 core, then this will suffice as the MEB conductor

Or does he have to run a 10mm^2 earth regardless of the supply cable size (ie in addition)?

This would only be required it the supply cable to the garage was <10mm²

3. Also he talks about 6 0r 10mm^2 cable......surely vastly oversized for his requirements. Without even bothering to get the tables out I would have thought 3core 2.5mm^2 would be more than adequate with as separate 10mm^2 earth run together in a duct or even overhead.

a 2.5mm² SWA with a 10.0mm² seperate earth would be fine.

4. Would you consider the shed to be an extraneous conductive part and need to be earthed?

Thats a bit more difficult, and would need to be assessed on a shed by shed basis.

If there is structural metal work into the ground then I'd probably say yes.

5. What would you personally consider as the best solution to this proposed installation?

Personally if there was an extraneous conductive part(s) then I'd export an earth, and probably go with a 10mm² SWA. It is less messing about, and gives future capacity.

It also avoides the additional precautions required for a TT installation.
 