I have a 5 bed, 3 bath Bovis built house 23 years old, we have lived here since new. The central heating system has been poor from Day 1 almost - it has a Potterton Netaheat Electronic 16/22 boiler which has run like clockwork with virtually no repairs needed over the entire time we have lived here. There are 19 radiators (some quite big ones) on the system. The heating is better upstairs than downstairs. The pump is Grundfos 16-50 130. Hot water has always been excellent - virtually impossible to run out. We have an auto bleed valve at the highest point in the system.
However, the radiators have always been, mostly, lukewarm and had required the system flushing at least every 2 years in order to keep them even at this level. (Very hard water area). About 5 years ago our plumber installed a pressure vessel and got rid of the previous gravity tank and this seems to have removed the need for flushing but the rads are still very poor in terms of heat output. There is no air in the system and I check the pressure regularly - the system has corrosion inhibitor in it but no magnatec device (one plumber suggested this may help but it has not been installed).
The upstairs radiator valves have to be virtually closed to get any heat at all in the downstairs rads and I have to be very careful to balance the smaller rads down to almost nothing in order to get any heat from the big ones.
I have had countless plumbers/heating engineers to look at it over the years - they all scratch their heads and offer the usual advice - new pump, power flushing, check the system balance, diverter valves, progressive rad bleeding, etc. etc. Nobody has been able to make any significant improvements or offer any revelations. Why I accepted the system in the first place when we bought the house from Bovis is beyond me, but it's a well insulated property and we have a mild climate down south so ... we put an extra jumper on when it gets cold.
Having now started to update and modify bathrooms and kitchen (floors up etc.) I have discovered that the majority of the system is plumbed in 15mm and the there are just 'tails' of 8mm microbore feeding the actual radiators. These tails vary in length from a few feet to several metres depending on where the rads are located. It appears to be a traditional layout of pipes apart from the microbore tails. I think this is a fairly rubbish way of plumbing the house but I would welcome anyone's comments.
I have, recently, replaced the microbore tails to 2 of the bathroom rads with 15mm (joining on to the existing 15mm incoming and outgoing pipework) and wonder upon wonder - we have 'proper' heat in these rads now !!
So ... is this a fluke ? or can I assume that I would be better to replace all of the 8mm with 15mm - it means all of the ceilings out of the ground floor as all the pipework is in the ceiling void (we have solid floors downstairs) but it might be worth it as we are thinking of selling the house and the poor heating is going to be noticed - or at least have to be identfied to a potential buyer.
I can do the pipework plumbing myself and it would be plastic for the runs across the ceiling void and copper down the walls - but I want to be sure that it is worthwhile before ripping the ceilings out. My present plumber (who has also failed to improve the heating) huffed and puffed and said it 'might be a good idea' when I phoned him. He told me that the microbore should come from a 'manifold' and then the pipes should all be of an equal length to all the radiators (clearly, in my house, this is not the case).
I would really like some clear advice. Sorry about the length of this post but I think you need to know as much as possible. Thanks everyone.
However, the radiators have always been, mostly, lukewarm and had required the system flushing at least every 2 years in order to keep them even at this level. (Very hard water area). About 5 years ago our plumber installed a pressure vessel and got rid of the previous gravity tank and this seems to have removed the need for flushing but the rads are still very poor in terms of heat output. There is no air in the system and I check the pressure regularly - the system has corrosion inhibitor in it but no magnatec device (one plumber suggested this may help but it has not been installed).
The upstairs radiator valves have to be virtually closed to get any heat at all in the downstairs rads and I have to be very careful to balance the smaller rads down to almost nothing in order to get any heat from the big ones.
I have had countless plumbers/heating engineers to look at it over the years - they all scratch their heads and offer the usual advice - new pump, power flushing, check the system balance, diverter valves, progressive rad bleeding, etc. etc. Nobody has been able to make any significant improvements or offer any revelations. Why I accepted the system in the first place when we bought the house from Bovis is beyond me, but it's a well insulated property and we have a mild climate down south so ... we put an extra jumper on when it gets cold.
Having now started to update and modify bathrooms and kitchen (floors up etc.) I have discovered that the majority of the system is plumbed in 15mm and the there are just 'tails' of 8mm microbore feeding the actual radiators. These tails vary in length from a few feet to several metres depending on where the rads are located. It appears to be a traditional layout of pipes apart from the microbore tails. I think this is a fairly rubbish way of plumbing the house but I would welcome anyone's comments.
I have, recently, replaced the microbore tails to 2 of the bathroom rads with 15mm (joining on to the existing 15mm incoming and outgoing pipework) and wonder upon wonder - we have 'proper' heat in these rads now !!
So ... is this a fluke ? or can I assume that I would be better to replace all of the 8mm with 15mm - it means all of the ceilings out of the ground floor as all the pipework is in the ceiling void (we have solid floors downstairs) but it might be worth it as we are thinking of selling the house and the poor heating is going to be noticed - or at least have to be identfied to a potential buyer.
I can do the pipework plumbing myself and it would be plastic for the runs across the ceiling void and copper down the walls - but I want to be sure that it is worthwhile before ripping the ceilings out. My present plumber (who has also failed to improve the heating) huffed and puffed and said it 'might be a good idea' when I phoned him. He told me that the microbore should come from a 'manifold' and then the pipes should all be of an equal length to all the radiators (clearly, in my house, this is not the case).
I would really like some clear advice. Sorry about the length of this post but I think you need to know as much as possible. Thanks everyone.