I've got a 10 year old combi boiler and for the last 3 years have used a Honeywell CM927 programmable thermostat, which, to be fair, does keep the room at a pretty constant temp.
I've read quite a few posts on the stat and understand a bit about the algorithm and how it fires to achieve the set point. And obviously, without weather comp, it fires either more frequently depending on how far off set point, to get the rads to dissipate just enough heat to achieve the set point.
However, what is pretty clear is the boiler obviously cycles a lot more than the case with the old conventional stat. Especially as it nears the set point. The boiler is pretty oversized being a combi, 31kwh output and rads only about 9kwh at most and the boiler only modulates to min 12.7kwh.
The defaults on the stat have been left as is, so the stat allows 6 cycles per hour (1 every 10 min) and ,min 1 min firing time.
Sometimes, when it is really cold in the morning, you can hear the boiler momentarily shut down after 10min and immediately like 1 second delay, come back on again so firing time obviously being calced at 10 min but it swithces on off and immediately back on.. But If the boiler had already been running and burner just stopped firing it will immediately provoke the boiler to refire after cycling on and off which seems a bit excessive and contrary to what the boiler would of been doing had it just been left uninterupted.
The boiler has a dip switch setting for min burner re-ignition period. It is selectable between 30 sec or 3 min via a dip switch.
So, to my queastion, Is there any value on choosing the higher value of 3 min? Would this make any difference with the stat momentary switch off and immediate switch ons?
As said, the boiler is 10 plus years, we have lived here 4.5 years. It has been fairly reliable in the scheme of things but has required a diverter valve group set, (understandable) and an ignition pcb. Wondering if the repeated firing cycles is not helping the latter?
Thanks.
I've read quite a few posts on the stat and understand a bit about the algorithm and how it fires to achieve the set point. And obviously, without weather comp, it fires either more frequently depending on how far off set point, to get the rads to dissipate just enough heat to achieve the set point.
However, what is pretty clear is the boiler obviously cycles a lot more than the case with the old conventional stat. Especially as it nears the set point. The boiler is pretty oversized being a combi, 31kwh output and rads only about 9kwh at most and the boiler only modulates to min 12.7kwh.
The defaults on the stat have been left as is, so the stat allows 6 cycles per hour (1 every 10 min) and ,min 1 min firing time.
Sometimes, when it is really cold in the morning, you can hear the boiler momentarily shut down after 10min and immediately like 1 second delay, come back on again so firing time obviously being calced at 10 min but it swithces on off and immediately back on.. But If the boiler had already been running and burner just stopped firing it will immediately provoke the boiler to refire after cycling on and off which seems a bit excessive and contrary to what the boiler would of been doing had it just been left uninterupted.
The boiler has a dip switch setting for min burner re-ignition period. It is selectable between 30 sec or 3 min via a dip switch.
So, to my queastion, Is there any value on choosing the higher value of 3 min? Would this make any difference with the stat momentary switch off and immediate switch ons?
As said, the boiler is 10 plus years, we have lived here 4.5 years. It has been fairly reliable in the scheme of things but has required a diverter valve group set, (understandable) and an ignition pcb. Wondering if the repeated firing cycles is not helping the latter?
Thanks.