Myson Apollo 30/50b

Joined
16 Jan 2008
Messages
4
Reaction score
0
Location
Berkshire
Country
United Kingdom
I have just installed a new O/H stat on the boiler, i had issues with the pilot light cutting out after 10 - 15mins, which seemed to do the trick. After a couple of days now the boiler is getting piping hot and now over heating, the expansion tank last night was like a sauna (red hot with steam), and the boiler sounds like someone flushing a toilet ( best to describe it), pipes have started banging. I have checked the pump which seems to be working fine, plenty of water in the expansion tank, wall t/s is operating the boiler properly. Everything seems to be ok on the H/W side, it seems to be happening on the C/H. Any ideas of what it might be? Your help is appreciated.
 
Sponsored Links
do you have a by-pass, TRVs, 3port or 2*2port valves and how long b4 the banging starts
 
I have TRV's downstairs and 2*2ports upstairs. It takes no longer than 45-1hr before the trouble starts. The boiler starts to sound like it has a large bubble inside it. The rads are very very hot also. Would Hi/Lo stats on the boiler play a part in this?
 
probably high stat fault, try setting switch to low and see what happens
 
Sponsored Links
Thanks for responding twgas. Because there was so much hot water and heat in the expansion tank, the first thing i did was drop it to low. Problem is still the same. Someone has suggested the circuit board on the boiler? what do you think?
 
dont remember ever seeing a PCB on 30/50B,
could be t/stats or wiring loom to stats, might also be gas valve not shutting off properly
 