Hi,
I have constructed an attached pergola roof with the following spec
- C24 2x6 rafters with spans between 4m and 4.8m
- C24 2x6 wall plates
- C24 2x6 bressummer
- bressummer supported on 100x100 posts at 3m spans and fixed to wall at one end
- rafter slope is ~5 degrees.
- rafters sitting on joist hangers at bressummer and wall plate
- pairs of 2x6 noggins between rafters
- 2x2 purlins @ 400mm centres above rafters
Most of the structure has been stood for a year, just with a tarp over it (plus some loose poly underneath for rigidity).
I would now like to finish it with a polycarbonate roof on but consulting some flat roof span tables, I can see that C24 2x6 can only support a 3m span (assuming 0.75kn/m2).
I think that the bressummer is also underspecced.
I believe that it may be possible to save the situation, with the following changes.
1) Rearrange the bressummer posts to set max span at 2 metres
2) Replace bressummer with 75x225 C24 timber, still on 100x100 posts
3) Add a further line of posts at the midpoint of the rafters, with 75x224 C24 timbers, to reduce rafter span to max of 2.4 metres.
Below is a sketch I originally did, but the structure now goes further to the left and attaches to a wall that is 90 degrees to the rear of the house, plus the rafters are 4m to the centre of the house, but 4.8m to the left and right, where the rear wall is receded.
I have also attached a couple of recent pics of the structure.
I am really loathed to run the extra line of posts at the midpoint of the rafters, but if I need to, then I will have to.
Any thoughts would be much appreciated.
I have constructed an attached pergola roof with the following spec
- C24 2x6 rafters with spans between 4m and 4.8m
- C24 2x6 wall plates
- C24 2x6 bressummer
- bressummer supported on 100x100 posts at 3m spans and fixed to wall at one end
- rafter slope is ~5 degrees.
- rafters sitting on joist hangers at bressummer and wall plate
- pairs of 2x6 noggins between rafters
- 2x2 purlins @ 400mm centres above rafters
Most of the structure has been stood for a year, just with a tarp over it (plus some loose poly underneath for rigidity).
I would now like to finish it with a polycarbonate roof on but consulting some flat roof span tables, I can see that C24 2x6 can only support a 3m span (assuming 0.75kn/m2).
I think that the bressummer is also underspecced.
I believe that it may be possible to save the situation, with the following changes.
1) Rearrange the bressummer posts to set max span at 2 metres
2) Replace bressummer with 75x225 C24 timber, still on 100x100 posts
3) Add a further line of posts at the midpoint of the rafters, with 75x224 C24 timbers, to reduce rafter span to max of 2.4 metres.
Below is a sketch I originally did, but the structure now goes further to the left and attaches to a wall that is 90 degrees to the rear of the house, plus the rafters are 4m to the centre of the house, but 4.8m to the left and right, where the rear wall is receded.
I have also attached a couple of recent pics of the structure.
I am really loathed to run the extra line of posts at the midpoint of the rafters, but if I need to, then I will have to.
Any thoughts would be much appreciated.