What about this,
The house where the RCD is tripping has a neutral to ground fault. With the incoming neutral at the same potential as ground this fault will not be passing any current so the RCD will not trip
Neighbour switches on a large motor with a high inrush current. The high in rush current along the network creates a transient potential spike on the network neutral. This raises the neutral above ground in houses in the area. The house with a neutral to ground fault will have a transient current through the fault and this coulr trip the RCD.
Adding a local ground rod to the incoming neutral would reduce the transient differences beten and maybe that was what the DNO did here
The house where the RCD is tripping has a neutral to ground fault. With the incoming neutral at the same potential as ground this fault will not be passing any current so the RCD will not trip
Neighbour switches on a large motor with a high inrush current. The high in rush current along the network creates a transient potential spike on the network neutral. This raises the neutral above ground in houses in the area. The house with a neutral to ground fault will have a transient current through the fault and this coulr trip the RCD.
Adding a local ground rod to the incoming neutral would reduce the transient differences beten and maybe that was what the DNO did here
They added a ground rod at the bas of the pole.- each time the DNO came and had a look at the pole connections, denied it was anything to do with them .... but the tripping stopped happening anyway.