Nest /Hive Glowworm Flexicom 30cx

Joined
6 Dec 2016
Messages
3
Reaction score
0
Country
United Kingdom
Hello I have a newish Flexicom 30cx I fitted a climbapro rf 2. I'm. Now looking to get a nest but I'm. Not sure if this is going to work with my Flexicom as I know the ebus is strange but I'm think the two wire to the nest could go in the 2 and 3 slot on the best and run it a a L + N.
 
Sponsored Links
So feed the nest with a 240 supply and R and F into 2 and 3 cheers
 
Sponsored Links
So feed the nest with a 240 supply and R and F into 2 and 3 cheers
The Nest Needs Live and Neutral taken from the boiler terminals.
The R terminal is the boiler switched Live so you need a permanent Live connected to the Nest 2 and connect boiler R to Nest 3.
The permanent Live on Nest 2 can either be a short wire link from the Nest L terminal or a wire from the L terminal in the boiler.
 
Last edited: