During a thunderstorm last week there a power outtage lasting a few seconds after a lighting strike to ground less than a mile from the location.
It was later discovered that the RCD in an out building had tripped. It would not reset until two items of equipment were unplugged. Investigation found the mains input filters on these two items were showing low impedance between Neutral and Earth terminals.
The outbuiding is fed TT with a pair of ground rods.
The cause of the fault is believed to be a severe potential difference between ground ( at the ground rod ) and the supply neutral as a result of the lightning strike and that this transient punched through the dialectric of the filter capacitors.
The extremely rapid rise of the transient voltage from a lightning strike means the internal inductance of the wound paper capacitors becomes very significant.
Is there a case for fitting fast acting transient absorbers between TT Neutrals and ground rods where the distance involved would create a significant voltage gradient across the ground. ?
It was later discovered that the RCD in an out building had tripped. It would not reset until two items of equipment were unplugged. Investigation found the mains input filters on these two items were showing low impedance between Neutral and Earth terminals.
The outbuiding is fed TT with a pair of ground rods.
The cause of the fault is believed to be a severe potential difference between ground ( at the ground rod ) and the supply neutral as a result of the lightning strike and that this transient punched through the dialectric of the filter capacitors.
The extremely rapid rise of the transient voltage from a lightning strike means the internal inductance of the wound paper capacitors becomes very significant.
Is there a case for fitting fast acting transient absorbers between TT Neutrals and ground rods where the distance involved would create a significant voltage gradient across the ground. ?