Hello,
I know there are similar questions previously, but would like to ask anyway:
I am replacing my current bathroom extractor with a new MANROSE CFD200s (with no timer). The Present extractor comes on when the light is operated from a light switch outside the room. There is fused switch.
I was going to just simply replace the olf fan with the newer fan.
Instructions say that a Double Pole Fused Spur must be used and fitted with a 3 amp fuse.......
How do I do this? I was hpoing there would have been a diagram in the box. There isn't.
Fan has two terminals. Neutral and Permanent Live.
Any advice would be most appreaciated.
Thanks ever so much