New Cooker and Hob
31 Oct 2010
Manchester
Hi, first post, hope someone can help.
Just purchased a new Baumatic built in oven B724SS, with max rated inputs 4.12KW. Instructions say, require 20 amp double pole switched fuse outlet with 3mm contact gap.
Also purchased Belling PBI 60 induction hob, max load 7.4KW (based on all 4 rings on at once). Instructions say must be installed using a multi pole control unit of 30 amp minimum.
My existing wiring is a 6mm cable from the CU which has a Hagar MT 132 fuse. This is currently wired into a standard neon switched cooker control unit with a plug socket.
My question is, if i get a Dual Appliance Outlet Plate to facilitate splitting the cable, can I put a new 45A Cooker panel switch for the hob only. In other words having 2 cooker switches running off the original 6mm cable?
Thnaks in anticapation. Gary
So you have 7.4kW + 4.2kW max load = 11.6 kW, or 50A if the power ratings were for 230V.
The proper way of doing this would be to use separate circuits for your hob and oven. You may probably be able to re-use the 6mm² cable for the hob, but you won't know until you have applied the necessary de-rating factors for cable fixing, grouping and voltage drop etc.
It would be notifiable also.
The oulet plate must be connected between the oven or hob and the isolation switch/CCU, and should not be used to provide a spur as you're suggesting.
May I suggest that an electrician may be the better route forward here?
Your existing circuit is good for the induction hob.
You'll need a new, separate 20A supply for the Oven.