Hi

I have just installed a new heated towel radiator onto a combi boiler system. The unit has filled up (spitting out of the air valve) however when the heating system is running the towel rail does not get hot.

Any ideas?

Many thanks
 
Sponsored Links
HI

Yes, first part checked. All other rads working fine, it's just this one

Many thanks
 
If it's sharing a leg with another radiator, that might have less resistance and the water's going there instead.

Try turning off other rads in the room or area.

If that helps, adjustment should allow you to balance the spread so they all get hot.
 
Sponsored Links
Thanks will try that today.

Is is worth turning off all other rads on the system and trying to run just the one that is not working?

Many thanks
 