New Honeywell V4073A1088 possible problem

Joined
23 Nov 2010
Messages
1
Reaction score
0
Country
United Kingdom
Hi - I have just had had a new Honeywell V4073A1088 valve installed (about 2 weeks ago) to sort out a heating problem I was having.

The heating refuses to switch off - even when slider switches programmer on boiler are set to OFF. I have had the programmer changed on the boiler - and it makes no difference - ie. the heating will not switch off - unless boiler is set to hot water first and thermostat dial is turned all the way off.

It has been suggested that the V4073A1088 valve could be stuck 'open'? I have checked the lever on it and it is set constantly to AUTO. I tried to move the lever manually - and found it extremely easy to slide back and forth. Could this problem be linked to the spring lever not installed properly?
Thanks
 
Sponsored Links
nomiwilts";p="1809123 said:
Hi - I have just had had a new Honeywell V4073A1088 valve installed (about 2 weeks ago) to sort out a heating problem I was having.


The indications are that the valve body has been installed the wrong way round, ie, hot water port to central heating and vice-versa.
 
The side marked "B" should go towards the cylinder heating coil !

Thats a very basic mistake. What was the calibre of the person who fitted the valve?

Tony
 