Sorry guys, i was reading your replys and saying what, but you would have needed a cyrstal ball,
It was fitted with 16 amp and i replaced with 10 amp
Sorry
Today i was fitting new light fittings in a new flat.
The company who carried out the install are members of the NICEIC.
But when i was checking the circuits i found the following,
1, Circuit wired in 1.00mm but supplied from a 10 amp type B breaker.
2, The lights have been looped at each light switch all the CPC are twisted together and in the one bit of earth sleeving.
Would you just note your findings on the minor works certificate or would you advise the customer to take this up with the main contractor of the housing project.
Have any of you guys came across these problems?
It was fitted with 16 amp and i replaced with 10 amp
Sorry
Today i was fitting new light fittings in a new flat.
The company who carried out the install are members of the NICEIC.
But when i was checking the circuits i found the following,
1, Circuit wired in 1.00mm but supplied from a 10 amp type B breaker.
2, The lights have been looped at each light switch all the CPC are twisted together and in the one bit of earth sleeving.
Would you just note your findings on the minor works certificate or would you advise the customer to take this up with the main contractor of the housing project.
Have any of you guys came across these problems?